    I'm having a dedicated electrical line installed soon for my B&K Reference 200.5 amp. Should I have the electrician install a 20 amp line or just a 15 amp line? Is this amp designed to work on a 20 amp line? If so, why does it have a regular 15 amp plug? The owners manual states it is important that it is plugged into " a dedicated line". Thanks for any info.
  • dyazdani
    Moderator Emeritus
    • Oct 2005
    • 7032

    #2
    According to the specs, the max current draw is 17.5 Amps... can't share a breaker with another component due to the current requirement so it seems...
    Danish

    Comment

    • dyazdani
      Moderator Emeritus
      • Oct 2005
      • 7032

      #3
      Oh, and the electrician can install a 20 amp breaker, proper Romex (12ga I think), and an outlet that is rated for 20 amps (but will accept a 15A plug). He/she should know what to do...
      Danish

      Comment

      • GregLett
        Senior Member
        • May 2005
        • 753

        #4
        Put in the 20A.
        Greg

        Comment

        • Chris D
          Moderator Emeritus
          • Dec 2000
          • 16877

          #5
          Agreed. Put in the 20A circuit. I had two dedicated 20A circuits run just to the equipment racks in my previous theater, and have four in my current equipmet room.
          Definitely want the power units getting all the juice they need.
          CHRIS

          Well, we're safe for now. Thank goodness we're in a bowling alley.
          - Pleasantville

          Comment

          • scarpi
            Member
            • Jul 2008
            • 87

            #6
            Thanks all, I'm going with the 20 amp line. :T

            Comment

            Working...
            Searching...Please wait.
            An unexpected error was returned: 'Your submission could not be processed because you have logged in since the previous page was loaded.

            Please push the back button and reload the previous window.'
            An unexpected error was returned: 'Your submission could not be processed because the token has expired.

            Please push the back button and reload the previous window.'
            An internal error has occurred and the module cannot be displayed.
            There are no results that meet this criteria.
            Search Result for "|||"