    Adding a Dedicated 20A Circuit

    I am looking at adding a 20A dedicated circuit for my HT. My dad is an electrician and will do all of the work, he's certainly not into HT by any means though...

    what are things to do and also to avoid when doing this..

    Thanks..
    Samsung UN60C6300 | Primare SP32 | Primare A30.7 | Oppo BDP-103 | PS Audio Quintet | AppleTV | ELAC 247 Black Edition | ELAC CC 241 Black Edition | B&W DM 600 S3 | SVS PC 13 Ultra | Straight Wire Virtuoso | Harmonic Technology Pro 9's | Black Sands Power Cords
  • mjb
    Super Senior Member
    • Mar 2005
    • 1485

    #2
    Use decent (perhaps over-rated) cable, I'd recomend a "slow-blow" 20 amp breaker so it doesn't trip when you turn your amps on, and make sure the ground is healthy.
    - Mike

    Main System:
    B&W 802D, HTM2D, SCMS
    Classé SSP-800, CA-2200, CA-5100

    Comment

    • Gianluca
      Member
      • Oct 2008
      • 90

      #3
      I installed an insulated ground orange plug which is usally installed in computer rooms. This type of plug has an insolated ground. The wire you would use has a hot,neutral,insolated ground and a bare ground. The plug itself is of much better quality and the equipement is grounded directly at the panel.

      Luca
      Sharp Aquos 40" 1080P| Rotel RSX 1056 | Classé CA-150 | Oppo BDP-83 | PS3 | APC H15 | B&W 603 S3 | B&W LCR 600 S3 | B&W 602 S3 | Sunfire True Sub Signature |

      Comment

      • wettou
        Ultra Senior Member
        • May 2006
        • 3398

        #4
        Originally posted by Armbender
        I am looking at adding a 20A dedicated circuit for my HT. My dad is an electrician and will do all of the work, he's certainly not into HT by any means though...

        what are things to do and also to avoid when doing this..

        Thanks..
        My electrician use wiring for Air-conditioning which sustain a 40A circuit that way no worries
        Farming looks mighty easy when your plow is a pencil, and you're a thousand miles from the corn field."Dwight D. Eisenhower

        Comment

        • Armbender
          Senior Member
          • Jul 2005
          • 265

          #5
          I keep reading that you should use 12awg wire. Any links to recomended wire?
          Samsung UN60C6300 | Primare SP32 | Primare A30.7 | Oppo BDP-103 | PS Audio Quintet | AppleTV | ELAC 247 Black Edition | ELAC CC 241 Black Edition | B&W DM 600 S3 | SVS PC 13 Ultra | Straight Wire Virtuoso | Harmonic Technology Pro 9's | Black Sands Power Cords

          Comment

          • wettou
            Ultra Senior Member
            • May 2006
            • 3398

            #6
            Originally posted by Armbender
            I keep reading that you should use 12awg wire. Any links to recomended wire?
            Thicker is better that way it doesn't melt as fast :B
            Farming looks mighty easy when your plow is a pencil, and you're a thousand miles from the corn field."Dwight D. Eisenhower

            Comment

            • Chris D
              Ultra Senior Member
              • Dec 2000
              • 16875

              #7
              Just regular 12-2 Romex will work fine.
              CHRIS

              Well, we're safe for now. Thank goodness we're in a bowling alley.
              - Pleasantville

              Comment

              • Armbender
                Senior Member
                • Jul 2005
                • 265

                #8
                Originally posted by Chris D
                Just regular 12-2 Romex will work fine.
                thanks...I think im going to add an ATL recepticle also..
                Samsung UN60C6300 | Primare SP32 | Primare A30.7 | Oppo BDP-103 | PS Audio Quintet | AppleTV | ELAC 247 Black Edition | ELAC CC 241 Black Edition | B&W DM 600 S3 | SVS PC 13 Ultra | Straight Wire Virtuoso | Harmonic Technology Pro 9's | Black Sands Power Cords

                Comment

                • Glen B
                  Super Senior Member
                  • Jul 2004
                  • 1106

                  #9
                  Originally posted by mjb
                  I'd recommend a "slow-blow" 20 amp breaker so it doesn't trip when you turn your amps on
                  North American household electrical does not have the option to select breakers with different trip curves.


                  Comment

                  • Briz vegas
                    Super Senior Member
                    • Mar 2005
                    • 1199

                    #10
                    I had a 6mm dedicated circuit installed in December. The only thing I did that does not seem to be mentioned here is having a separate 20amp breaker to the rest of the house.

                    Thicker is better as the amp is better able to draw current as required. When an amp wants current it wants it "yesterday".

                    Very happy with the results.
                    Mac 8gb SSD Audirvana ->Weiss INT202 firewire interface ->Naim DAC & XPS2 DR->Conrad Johnson CT5 & LP70S-> Vivid B1s. Nordost Valhalla cables & resonance management. (Still waiting for Paul Hynes PS:M)
                    Siamese :evil: :twisted:

                    Comment

                    • Armbender
                      Senior Member
                      • Jul 2005
                      • 265

                      #11
                      Hopefully Ill be able to get this started soon..Very eager to see the results..
                      Samsung UN60C6300 | Primare SP32 | Primare A30.7 | Oppo BDP-103 | PS Audio Quintet | AppleTV | ELAC 247 Black Edition | ELAC CC 241 Black Edition | B&W DM 600 S3 | SVS PC 13 Ultra | Straight Wire Virtuoso | Harmonic Technology Pro 9's | Black Sands Power Cords

                      Comment

                      • NonSense
                        Senior Member
                        • Nov 2003
                        • 138

                        #12
                        Armbender

                        IMO when doing the work to fish one circuit, you might as well run two. You will then have the option to have your amps on one and the source equipment on the other. If you only have space for one receptacle, the upper and lower half may be split. Hubbel make excellent off the shelf hospital grade receptacles. They really bite into the plugs. Also available with isolated grounds. (Lots of exotic stuff out there, but the Hubbels are very good at a good price. They beat leviton by a large margin) If running two circuits you will want to use the same voltage pole in the panel. Most panels alternate poles moving up and down the slots to allow for double pole breakers for your stove, dryer, AC etc. There is not risk, but best to keep them the same.
                        Bruce

                        Comment

                        • Armbender
                          Senior Member
                          • Jul 2005
                          • 265

                          #13
                          Originally posted by NonSense
                          Armbender

                          IMO when doing the work to fish one circuit, you might as well run two. You will then have the option to have your amps on one and the source equipment on the other. If you only have space for one receptacle, the upper and lower half may be split. Hubbel make excellent off the shelf hospital grade receptacles. They really bite into the plugs. Also available with isolated grounds. (Lots of exotic stuff out there, but the Hubbels are very good at a good price. They beat leviton by a large margin) If running two circuits you will want to use the same voltage pole in the panel. Most panels alternate poles moving up and down the slots to allow for double pole breakers for your stove, dryer, AC etc. There is not risk, but best to keep them the same.
                          thanks!...excellent info..

                          I wasnt able to run the line, not without tearing up my walls..i was hoping to have easy access to fish the lines through but it wasnt the case..so instead i installed an ATL 1000cu recepticle...
                          Samsung UN60C6300 | Primare SP32 | Primare A30.7 | Oppo BDP-103 | PS Audio Quintet | AppleTV | ELAC 247 Black Edition | ELAC CC 241 Black Edition | B&W DM 600 S3 | SVS PC 13 Ultra | Straight Wire Virtuoso | Harmonic Technology Pro 9's | Black Sands Power Cords

                          Comment

                          • scarpi
                            Member
                            • Jul 2008
                            • 87

                            #14
                            I use my dedicated 20 amp line only for my B&K power amp. The rest of the gear is plugged into the living room house circuit where my system is. Of course all my gear except my power amp is run through a Panamax Max 5510 power conditioner. The power amp is run through its own 20amp Panamax high current surge suppressor at the wall outlet. That way the whole system is protected. I once had a Sony tv damaged by a power surge so I learned that it is a good idea to protect your gear. :T

                            Comment

                            • Chris D
                              Ultra Senior Member
                              • Dec 2000
                              • 16875

                              #15
                              Agreed. TWO dedicated 20A circuits was a standard spec in my previous home theater to the homebuilder. In the end, I only wish I had spec'd out 4 instead of 2.

                              If there's one thing I've found, I always run out of plugs. And I'd rather plug directly into the source, or a conditioner at least, than doing any sort of extensions.
                              CHRIS

                              Well, we're safe for now. Thank goodness we're in a bowling alley.
                              - Pleasantville

                              Comment

                              • Armbender
                                Senior Member
                                • Jul 2005
                                • 265

                                #16
                                Originally posted by Chris D
                                Agreed. TWO dedicated 20A circuits was a standard spec in my previous home theater to the homebuilder. In the end, I only wish I had spec'd out 4 instead of 2.

                                If there's one thing I've found, I always run out of plugs. And I'd rather plug directly into the source, or a conditioner at least, than doing any sort of extensions.
                                definately something to think about when I do have an opportunity to develop my own dedicated HT
                                Samsung UN60C6300 | Primare SP32 | Primare A30.7 | Oppo BDP-103 | PS Audio Quintet | AppleTV | ELAC 247 Black Edition | ELAC CC 241 Black Edition | B&W DM 600 S3 | SVS PC 13 Ultra | Straight Wire Virtuoso | Harmonic Technology Pro 9's | Black Sands Power Cords

                                Comment

                                • Wayne A. Pflughaupt
                                  Member
                                  • Jun 2002
                                  • 69

                                  #17

                                  Originally posted by Chris D
                                  Agreed. TWO dedicated 20A circuits was a standard spec in my previous home theater to the homebuilder. In the end, I only wish I had spec'd out 4 instead of 2.

                                  If there's one thing I've found, I always run out of plugs. And I'd rather plug directly into the source, or a conditioner at least, than doing any sort of extensions.
                                  While the technical definition of a dedicated circuit means it feeds a single duplex outlet, there’s no reason why you couldn’t install additional outlets as needed on the circuit. I installed two circuits in my previous home, with each feed going to a “quadbox” – i.e., a box with dual outlets. That gave me eight plugs total, which was plenty for the equipment I had at the time.

                                  Regards,
                                  Wayne A. Pflughaupt

                                  Comment

                                  • Chris D
                                    Ultra Senior Member
                                    • Dec 2000
                                    • 16875

                                    #18
                                    Absolutely right. You're going to want at least ONE dedicated 20A circuit just for the equipment, but since high-powered theaters have some very strong amps and such, I would say you want to run two. Three is even better, and four would be more than I think anybody would possibly need, even with multiple tactile transducer amplifiers added in on top of the other stuff. Each circuit could certainly terminate in two or three quad-plug outlet boxes. I would just make sure each outlet box is labeled as to which circuit it's on, especially if they're placed right next to each other or vertically on a wall in a row.
                                    CHRIS

                                    Well, we're safe for now. Thank goodness we're in a bowling alley.
                                    - Pleasantville

                                    Comment

                                    Related Topics

                                    Collapse

                                    • Saurav
                                      Weird ground loop problem
                                      by Saurav
                                      Well, weird for me, at least. I got a PE plate amp some time back, and it's hummed from the first day I've hard it. Recently I spent some time trying to narrow it down. Here's what I know so far:

                                      * There's no video/cable in the system, and I added power strips and cables so everything...
                                      15 August 2008, 13:01 Friday
                                    • CWD
                                      RSP-1068 and ground loop problems
                                      by CWD
                                      [This is a long post, but it may be helpful to others that may have to deal with similar problems....]

                                      I upgraded from a Denon AVR-2700 receiver to the Outlaw Audio 755 amplifier+Rotel RSP-1068 in that order, in two steps, about 6 months apart. When the Outlaw amplifer showed up with...
                                      20 June 2004, 10:11 Sunday
                                    • EAmin
                                      20A dedicated circuits in my HT
                                      by EAmin
                                      I'm looking into putting in several dedicated 20A circuits. I need some help deciding how many dedicated circuits I need. I will have 4 amps including 2 sub amplifiers --- see below.

                                      (1) Rotel RB-1090: 380 X 2, Power Consumption: 800 Watts
                                      (1) Rotel RMB-1095: 200 X 5 Power Consumption:...
                                      23 February 2005, 21:38 Wednesday
                                    • Brandon B
                                      Yet another ground hum . . .
                                      by Brandon B
                                      OK here's one I can't figure.

                                      Got a rack ful omc stuff, and the only place I get any noise is from my sub (ground hum). To make it worse, it is only when my Symmetrix 551E eq iss in engaged mode.

                                      In other words, no hum at all when the system is used with the eq in the loop...
                                      18 July 2002, 09:17 Thursday
                                    • Jim-surround
                                      Ground Loop
                                      by Jim-surround
                                      I need some advice for a cheap ground loop isolator/filter. Seems I'm getting some hum from my DVD player. Everything is plugged into 1 circuit and in phase so that's not it. Probably got a plug(s) wired backwards somewhere in the house. I'm not really inclined to go through all the wiring to find it...
                                      01 March 2005, 14:12 Tuesday
                                    • Loading...
                                    • No more items.
                                    Working...
                                      Searching...Please wait.
                                      An unexpected error was returned: 'Your submission could not be processed because you have logged in since the previous page was loaded.

                                      Please push the back button and reload the previous window.'
                                      An unexpected error was returned: 'Your submission could not be processed because the token has expired.

                                      Please push the back button and reload the previous window.'
                                      An internal error has occurred and the module cannot be displayed.
                                      There are no results that meet this criteria.
                                      Search Result for "|||"